    Default GFCI Part #2

    Okay well the last two weeks have been interesting. I received a power head from Shagman that was shocking him and ran into all sorts of problems with it not tripping GFCI receptacles. It wasn’t until I let it sit a few days in water did it rear its ugly head to where it leaked enough current to trip the GFCI with help from a grounding probe. Because my equipment is not sensitive to pick up low amounts of current I was not able to check to see what or how much current it took to finally trip the GFCI receptacles and breaker. They should trip with 4 to 6 milli-amps.
    The following are my test results;
    Bad pump and nicked cord on pump
    At first I was getting 48 volts and no tripping even with a grounding probe
    I was getting a slight tingle when I placed my finger in the water. With a ground probe the shock was eliminated
    Used several GFCI receptacles and still no tripping
    Sealed the back of the pump with silicone thinking I could seal the pump, tested it several days later and it seemed to work. Voltage was down and no shocking.
    Left the pump and cord in the water for several days and the animal reared its ugly head again
    This time on the test I had sixty-five volts and a slight shock being bare foot on a tile floor (DO NOT TRY THIS PLEASE) and no trip on the GFCI receptacles or breaker.
    Added a ground probe to the water and a immediate trip on receptacles and breaker
    I also used an Arc Fault Breaker and no trip even with the grounding probe installed

    In following up, a grounding probe is a must for protection to get GFCI receptacles to work properly if the power head does not contain one plus the protection you get from stray voltage from open lamps and internal pumps. Since I did not have a bad power head with a grounding conductor I can not tell you for sure if you would be protected not using a grounding probe? Using a GFCI with out the grounding probe you may still get a shock when placing your hand into your aquarium.

    Remember to always check/test your GFCI to see that it works. Nothing worse than thinking you are protected when you are not.

    Also you are not protected using just Arc Fault breakers!

    On another project I ran into only having five volts and getting an extreme shock becuse the home did not have a sufficient ground rod at the service and it was using the aquarium for a ground.

    Before using a grounding probe you must check or have an electrician check to see if your service is well grounded and also check the receptacle you will be installing the probe to.

    Materials:
    Pass and Seymour GFCI receptacles
    General Electric Panel
    General Electric GFCI Breaker
    General Electric AFCI Breaker
    Bad Power Head
    Grounding Probe
    Bucket of Water
    Fluke Meter

  2. #2
    Join Date
    05-23-2009
    Location
    LaVernia, Texas
    Posts
    8,622

    Default

    Quote Originally Posted by alton View Post
    Remember to always check/test your GFCI to see that it works. Nothing worse than thinking you are protected when you are not.
    How?
    Karin



  3. #3
    Join Date
    05-08-2009
    Location
    NE San Antonio
    Posts
    1,883

    Default

    It should have a test button on it that trips it.

  4. #4

    Default

    Wow, Alton.... thanks for documenting all this. I'm hoping that if I read it 25 more times I will understand all this perfectly some day!
    http://www.millan.net/minimations/sm...riumsmile1.gif - Kristy and Mike -

    210 g reef tank started 3/15/08; 20 g hex reef tank started 1/3/08, ended 3/30/14

    "I must be a mermaid.... I have no fear of depths and a great fear of shallow living." - Anais Nin
    "To travel is to take a journey into yourself." - Danny Kaye

  5. #5
    Join Date
    05-23-2009
    Location
    LaVernia, Texas
    Posts
    8,622

    Default

    Quote Originally Posted by BSJF View Post
    It should have a test button on it that trips it.
    oh you mean the one that says 'press here to test' ? lol

    I figured if they are so often not responding correctly, the test button could be faulty too (as in it trips for the test button but not for the actual appliance)

    By the way I got my two dedicated new aquarium circuits with GFCI wired at the breaker box this weekend.
    Karin



  6. #6
    Join Date
    07-19-2009
    Location
    San Antonio (Stone Oak)
    Posts
    751

    Default

    Quote Originally Posted by Europhyllia View Post
    oh you mean the one that says 'press here to test' ? lol

    I figured if they are so often not responding correctly, the test button could be faulty too (as in it trips for the test button but not for the actual appliance)

    By the way I got my two dedicated new aquarium circuits with GFCI wired at the breaker box this weekend.
    Yes, the test button/switch could be faulty - a GFCI tester will accurately tell you if that's the case - or if something isn't connected correctly. I borrowed one from an electrician - don't know how much they cost?

    Thanks for the info. Alton, I'm definitely getting a grounding probe...only prob is I get distracted everytime I go to the LFS
    -Terry
    8 gal. bio-cube

  7. #7

    Default

    Quote Originally Posted by Kristy View Post
    Wow, Alton.... thanks for documenting all this. I'm hoping that if I read it 25 more times I will understand all this perfectly some day!
    Maybe this topic could be added to a future MAAST meeting along with something else to make it a complete meeting? Maybe add UPS systems and other electrical products that protect our systems to the list?

  8. #8
    Join Date
    05-23-2009
    Location
    LaVernia, Texas
    Posts
    8,622

    Default

    That would be great!
    Karin



  9. #9

    Default

    Great idea.... Water + electricity = disaster plan for dummies!!!

  10. #10

    Default

    Quote Originally Posted by Kristy View Post
    Great idea.... Water + electricity = disaster plan for dummies!!!
    Hey this dummy is careful when doing stupid things like this. I did not drink a beer until afterwards. GFCI Plug Testers are $35 from Graybar, I thought Home Depot had them?

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •